Learn about the options to monitor your Octavia Load Balancer.
The Public Cloud Load Balancer provides two ways to monitor your Load Balancers: You can either query an API to get usage statistics or configure a Prometheus listener that can be scraped by your Prometheus infrastructure to gather metrics.
Requirements:
Instructions
Monitoring using CLI
The Load Balancer service aggregates these statistics and makes them available via the OpenStack API. Those statistics are available at the Load Balancer or listener level.
Load Balancer statistics can be queried using the OpenStack Client. They include metrics for all the listeners configured for the queried Load Balancer.
Individual listener statistics can also be queried using the OpenStack Client.
Monitoring with Prometheus
To add a Prometheus endpoint on a Public Cloud Load Balancer, create a listener with a PROMETHEUS
protocol. This will enable the /metrics
endpoint which listens on all the interfaces from your load balancer by default. This means that if your load balancer is using a Floating IP, by default the /metrics
endpoint will be opened to the internet. To avoid that, we advise setting the allowed_cidrs
option to protect your metrics, for example with the CIDR of the subnet where the load balancer is spawned.
This listener type provides the same features as the "regular" listeners but does not support attaching pools or L7 policies. All metrics will be identified by the Octavia object ID (UUID) of the resources.
Create a Prometheus listener via the OVHcloud Control Panel
From the OVHcloud Control Panel:
- Select
Public Cloud
from the top navigation bar. - In the left-hand menu under Network, select
Load Balancer
. - Select the
name
of the load balancer.
- Select the
Listeners
tab. - Click
+ Add a listener
. - Fill in a name, select Prometheus as the Protocol, and choose a Port (different from the already existing listener ports of your Load Balancer).
The default pool is grayed out because the Prometheus listener does not need a pool, unlike the other types of listeners.
- Click
Add
to trigger the listener creation.
The new listener is added to the listeners list.
Create a Prometheus listener via OpenStack GUI (Horizon)
Log in to Horizon using this guide.
Click Network
and then Load Balancers
. The Load Balancer list is displayed.
Click on the load balancer name
. The load balancer details page is then displayed.
Click the Listeners
tab and then Create Listener
.
On the listener creation page, fill in the Name and switch the Protocol to PROMETHEUS
. The port will be set to a default value that you can change if needed.
Click Create Listener
.
Create a Prometheus listener via OpenStack CLI
To create a Prometheus endpoint on port 9100 for Load Balancer lb1, you would run the following command:
Note that you should add the --allowed-cidr
option to filter the listener to a specific network.
Create a Prometheus listener via Terraform
The resource openstack_lb_listener_v2 from the OpenStack provider enables you to configure a Prometheus listener. The following snippet is extracted from a full example available on GitHub that you can adapt to your needs.
Configure Prometheus to collect your metrics
Once the PROMETHEUS
listener is ACTIVE
, you can configure Prometheus to collect metrics from the Load Balancer by updating the prometheus.yml
file.
prometheus.yml
file. Otherwise, you must add a public Floating IP to your load balancer and use it as the target IP.
Example prometheus.yml
file:
For more information on setting up Prometheus, see the Prometheus project website.
You can connect Grafana to the Prometheus instance to provide additional graphing and dashboard capabilities. A Grafana dashboard for Octavia Load Balancers is available here.
The metrics have the following naming format:
-
octavia_loadbalancer_xxx
oroctavia_memory_pool_xxx
metrics are global to the load balancer -
octavia_listener_xxx
metrics are instantiated per listener using the label {listener=ID} -
octavia_pool_xxx
metrics are instantiated per pool using the label {pool=ID} -
octavia_member_xxx
metrics are instantiated per member using the label {member=ID}
Metric | Description |
---|---|
octavia_loadbalancer_cpu | Load balancer CPU utilization (percentage). |
octavia_loadbalancer_memory | Load balancer memory utilization (percentage). |
octavia_memory_pool_allocated_bytes | Total amount of memory allocated in the memory pools (in bytes). |
octavia_memory_pool_used_bytes | Total amount of memory used in the memory pools (in bytes). |
octavia_memory_pool_failures_total | Total number of failed memory pool allocations. |
octavia_loadbalancer_max_connections | Maximum number of concurrent connections. |
octavia_loadbalancer_current_connections | Number of active sessions. |
octavia_loadbalancer_connections_total | Total number of created sessions. |
octavia_loadbalancer_requests_total | Total number of requests (TCP or HTTP). |
octavia_loadbalancer_max_ssl_connections | Configured maximum number of concurrent SSL connections. |
octavia_loadbalancer_current_ssl_connections | Number of active SSL connections. |
octavia_loadbalancer_ssl_connections_total | Total number of opened SSL connections. |
octavia_loadbalancer_current_connection_rate | Current number of connections per second over last elapsed second. |
octavia_loadbalancer_limit_connection_rate | Configured maximum number of connections per second. |
octavia_loadbalancer_max_connection_rate | Maximum observed number of connections per second. |
octavia_loadbalancer_current_session_rate | Current number of sessions per second over last elapsed second. |
octavia_loadbalancer_limit_session_rate | Configured maximum number of sessions per second. |
octavia_loadbalancer_max_session_rate | Maximum observed number of sessions per second. |
octavia_loadbalancer_current_ssl_rate | Current number of SSL sessions per second over last elapsed second. |
octavia_loadbalancer_limit_ssl_rate | Configured maximum number of SSL sessions per second. |
octavia_loadbalancer_max_ssl_rate | Maximum observed number of SSL sessions per second. |
octavia_loadbalancer_current_frontend_ssl_key_rate | Current frontend SSL Key computation per second over last elapsed second. |
octavia_loadbalancer_max_frontend_ssl_key_rate | Maximum observed frontend SSL Key computation per second. |
octavia_loadbalancer_current_backend_ssl_key_rate | Current backend SSL Key computation per second over last elapsed second. |
octavia_loadbalancer_max_backend_ssl_key_rate | Maximum observed backend SSL Key computation per second. |
octavia_loadbalancer_ssl_cache_lookups_total | Total number of SSL session cache lookups. |
octavia_loadbalancer_ssl_cache_misses_total | Total number of SSL session cache misses. |
octavia_loadbalancer_http_comp_bytes_in_total | Number of bytes per second over last elapsed second, before http compression. |
octavia_loadbalancer_http_comp_bytes_out_total | Number of bytes per second over last elapsed second, after http compression. |
octavia_loadbalancer_limit_http_comp | Configured maximum input compression rate in bytes. |
octavia_loadbalancer_listeners | Current number of active listeners. |
octavia_loadbalancer_dropped_logs_total | Total number of dropped logs. |
octavia_listener_status | Current status of the listener. 0=OFFLINE, 1=ONLINE, 2=DEGRADED. |
octavia_listener_current_sessions | Current number of active sessions. |
octavia_listener_max_sessions | Maximum observed number of active sessions. |
octavia_listener_limit_sessions | Configured session limit. |
octavia_listener_sessions_total | Total number of sessions. |
octavia_listener_limit_session_rate | Configured limit on new sessions per second. |
octavia_listener_max_session_rate | Maximum observed number of sessions per second. |
octavia_listener_connections_rate_max | Maximum observed number of connections per second. |
octavia_listener_connections_total | Total number of connections. |
octavia_listener_bytes_in_total | Current total of incoming bytes. |
octavia_listener_bytes_out_total | Current total of outgoing bytes. |
octavia_listener_requests_denied_total | Total number of denied requests. |
octavia_listener_responses_denied_total | Total number of denied responses. |
octavia_listener_request_errors_total | Total number of request errors. |
octavia_listener_denied_connections_total | Total number of requests denied by connection rules. |
octavia_listener_denied_sessions_total | Total number of requests denied by session rules. |
octavia_listener_failed_header_rewriting_total | Total number of failed header rewriting rules. |
octavia_listener_http_requests_rate_max | Maximum observed number of HTTP requests per second. |
octavia_listener_http_requests_total | Total number of HTTP requests received. |
octavia_listener_http_responses_total | Total number of HTTP responses. |
octavia_listener_intercepted_requests_total | Total number of intercepted HTTP requests. |
octavia_listener_http_cache_lookups_total | Total number of HTTP cache lookups. |
octavia_listener_http_cache_hits_total | Total number of HTTP cache hits. |
octavia_listener_http_comp_bytes_in_total | Total number of HTTP response bytes fed to the compressor. |
octavia_listener_http_comp_bytes_out_total | Total number of HTTP response bytes emitted by the compressor. |
octavia_listener_http_comp_bytes_bypassed_total | Total number of bytes that bypassed the HTTP compressor (CPU/BW limit). |
octavia_listener_http_comp_responses_total | Total number of HTTP responses that were compressed. |
octavia_pool_status | Current status of the pool. 0=OFFLINE, 1=ONLINE. |
octavia_pool_current_sessions | Current number of active sessions. |
octavia_pool_max_sessions | Maximum observed number of active sessions. |
octavia_pool_limit_sessions | Configured session limit. |
octavia_pool_sessions_total | Total number of sessions. |
octavia_pool_max_session_rate | Maximum observed number of sessions per second. |
octavia_pool_last_session_seconds | Number of seconds since last session assigned to a member. |
octavia_pool_current_queue | Current number of queued requests. |
octavia_pool_max_queue | Maximum observed number of queued requests. |
octavia_pool_connection_attempts_total | Total number of connection establishment attempts. |
octavia_pool_connection_reuses_total | Total number of connection reuses. |
octavia_pool_bytes_in_total | Current total of incoming bytes. |
octavia_pool_bytes_out_total | Current total of outgoing bytes. |
octavia_pool_queue_time_average_seconds | Avg. queue time for last 1024 successful connections. |
octavia_pool_connect_time_average_seconds | Avg. connect time for last 1024 successful connections. |
octavia_pool_response_time_average_seconds | Avg. response time for last 1024 successful connections. |
octavia_pool_total_time_average_seconds | Avg. total time for last 1024 successful connections. |
octavia_pool_max_queue_time_seconds | Maximum observed time spent in the queue |
octavia_pool_max_connect_time_seconds | Maximum observed time spent waiting for a connection to complete |
octavia_pool_max_response_time_seconds | Maximum observed time spent waiting for a member response. |
octavia_pool_max_total_time_seconds | Maximum observed total request+response time (request+queue+connect+response+processing) |
octavia_pool_requests_denied_total | Total number of denied requests. |
octavia_pool_responses_denied_total | Total number of denied responses. |
octavia_pool_connection_errors_total | Total number of connection errors. |
octavia_pool_response_errors_total | Total number of response errors. |
octavia_pool_retry_warnings_total | Total number of retry warnings. |
octavia_pool_redispatch_warnings_total | Total number of redispatch warnings. |
octavia_pool_failed_header_rewriting_total | Total number of failed header rewriting warnings. |
octavia_pool_client_aborts_total | Total number of data transfers aborted by the client. |
octavia_pool_member_aborts_total | Total number of data transfers aborted by the server. |
octavia_pool_active_members | Current number of active members. |
octavia_pool_backup_members | Current number of backup members. |
octavia_pool_check_up_down_total | Total number of UP->DOWN transitions. |
octavia_pool_check_last_change_seconds | Number of seconds since the last UP<->DOWN transition. |
octavia_pool_downtime_seconds_total | Total downtime (in seconds) for the pool. |
octavia_pool_loadbalanced_total | Total number of times a pool was selected, either for new sessions, or when redispatching. |
octavia_pool_http_requests_total | Total number of HTTP requests received. |
octavia_pool_http_responses_total | Total number of HTTP responses. |
octavia_pool_http_cache_lookups_total | Total number of HTTP cache lookups. |
octavia_pool_http_cache_hits_total | Total number of HTTP cache hits. |
octavia_pool_http_comp_bytes_in_total | Total number of HTTP response bytes fed to the compressor. |
octavia_pool_http_comp_bytes_out_total | Total number of HTTP response bytes emitted by the compressor. |
octavia_pool_http_comp_bytes_bypassed_total | Total number of bytes that bypassed the HTTP compressor (CPU/BW limit). |
octavia_pool_http_comp_responses_total | Total number of HTTP responses that were compressed. |
octavia_member_status | Current status of the member. 0=ERROR, 1=ONLINE, 2=OFFLINE, 3=DRAIN. |
octavia_member_current_sessions | Current number of active sessions. |
octavia_member_max_sessions | Maximum observed number of active sessions. |
octavia_member_limit_sessions | Configured session limit. |
octavia_member_sessions_total | Total number of sessions. |
octavia_member_max_session_rate | Maximum observed number of sessions per second. |
octavia_member_last_session_seconds | Number of seconds since last session assigned to the member. |
octavia_member_current_queue | Current number of queued requests. |
octavia_member_max_queue | Maximum observed number of queued requests. |
octavia_member_queue_limit | Configured maxqueue for the member (0 meaning no limit). |
octavia_member_bytes_in_total | Current total of incoming bytes. |
octavia_member_bytes_out_total | Current total of outgoing bytes. |
octavia_member_queue_time_average_seconds | Avg. queue time for last 1024 successful connections. |
octavia_member_connect_time_average_seconds | Avg. connect time for last 1024 successful connections. |
octavia_member_response_time_average_seconds | Avg. response time for last 1024 successful connections. |
octavia_member_total_time_average_seconds | Avg. total time for last 1024 successful connections. |
octavia_member_max_queue_time_seconds | Maximum observed time spent in the queue |
octavia_member_max_connect_time_seconds | Maximum observed time spent waiting for a connection to complete |
octavia_member_max_response_time_seconds | Maximum observed time spent waiting for a member response. |
octavia_member_max_total_time_seconds | Maximum observed total request+response time (request+queue+connect+response+processing) |
octavia_member_connection_attempts_total | Total number of connection establishment attempts. |
octavia_member_connection_reuses_total | Total number of connection reuses. |
octavia_member_responses_denied_total | Total number of denied responses. |
octavia_member_connection_errors_total | Total number of connection errors. |
octavia_member_response_errors_total | Total number of response errors. |
octavia_member_retry_warnings_total | Total number of retry warnings. |
octavia_member_redispatch_warnings_total | Total number of redispatch warnings. |
octavia_member_failed_header_rewriting_total | Total number of failed header rewriting warnings. |
octavia_member_client_aborts_total | Total number of data transfers aborted by the client. |
octavia_member_server_aborts_total | Total number of data transfers aborted by the server. |
octavia_member_weight | Member weight. |
octavia_member_check_failures_total | Total number of failed check (Only counts checks failed when the member is up). |
octavia_member_check_up_down_total | Total number of UP->DOWN transitions. |
octavia_member_downtime_seconds_total | Total downtime (in seconds) for the member. |
octavia_member_check_last_change_seconds | Number of seconds since the last UP<->DOWN transition. |
octavia_member_current_throttle | Current throttle percentage for the member, when slowstart is active, or no value if not in slowstart. |
octavia_member_loadbalanced_total | Total number of times a member was selected, either for new sessions, or when redispatching. |
octavia_member_http_responses_total | Total number of HTTP responses. |
octavia_member_idle_connections_current | Current number of idle connections available for reuse |
octavia_member_idle_connections_limit | Limit on the number of available idle connections |