This guide introduces Metro Availability, which provides an automated disaster recovery plan.
- Access to your clusters via Prism Central
- You need to have three Nutanix clusters within the OVHcloud infrastructure with Pack Advanced licenses if you have a package offer on both clusters in the P.R.A. These three clusters will need to be at remote sites for maximum security.
- You must have less than 5 ms of latency between the two replicated clusters. Please note that latency is not covered by SLAs.
Introduction
We will set up a two-way disaster recovery plan between two clusters with this hardware:
- A Nutanix cluster in Datacenter 1, with virtual machines replicated in Datacenter 2.
- A Nutanix cluster in Datacenter 2, with virtual machines replicated in Datacenter 1.
- A Nutanix cluster in Datacenter 3, with Prism Central to serve as a witness in the disaster recovery plan.
We will only use one vRack, which will contain:
- The three Nutanix clusters.
- Load balancers.
- Additional IP addresses on the rtvRack.
Below is the diagram showing the three sites:
Step 1.1 Interconnection of the three clusters
Step 1.2 Delete the Prism Central records for the Datacenter 1 and Datacenter 2 clusters
Step 1.3 Register both clusters on Prism Central in Datacenter 3
Step 1.4 Adding IP Addresses for iSCSI Connections on All Three Clusters
Step 1.5 Creating two Storage Containers
Step 1.6 Move virtual machines to the Storage Container
Step 1.7 Creation of a category to be used when implementing the P.R.A.
Step 1.8 Add virtual machines in categories
Step 1.9 Setting up synchronous replications between Datacenter 1 and Datacenter 2
Step 1.10 Create Subnets for Disaster Recovery Plan
Step 1.11 Implementation of disaster recovery plans
Step 2 Validate Disaster Recovery Plan
Step 2.1 Monitoring the Disaster Recovery Plan
Step 2.2 Live migration of virtual machines from Datacenter 1 to Datacenter 2
Step 2.3 Operations after a migration
Step 2.4 Execute the Disaster Recovery Plan in Real Condition
We will implement this disaster recovery plan step by step.
The cluster configuration information used in our guide is as follows:
Datacenter 1 cluster:
- Server 1: VM address CVM
192.168.0.21
, hypervisor IP address AHV192.168.0.1
. - Server 2: VM address CVM
192.168.0.22
, hypervisor IP address AHV192.168.0.2
. - Server 3: VM address CVM
192.168.0.23
, hypervisor IP address AHV192.168.0.3
. - Prism Element virtual address:
192.168.0.100
. - Prism Element iSCSI address:
192.168.0.102
. - Prism Central IP address:
192.168.0.101
. - Gateway:
192.168.3.254
. - Mask:
255.255.252.0
- Cluster version:
6.5
Datacenter 2 cluster:
192.168.1.21
, hypervisor IP address AHV192.168.1.1
192.168.1.22
, hypervisor IP address AHV192.168.1.2
192.168.1.23
, hypervisor IP address AHV192.168.1.3
192.168.1.100
192.168.1.102
192.168.1.101
. - Gateway:
192.168.3.254
. - Mask:
255.255.252.0
- Cluster version:
6.5
Datacenter 3 Cluster:
192.168.2.21
, hypervisor IP address AHV192.168.2.1
192.168.2.22
, hypervisor IP address AHV192.168.2.2
192.168.2.23
, hypervisor IP address AHV192.168.2.3
192.168.2.101
192.168.2.102
192.168.2.100
. - Gateway:
192.168.3.254
. - Mask:
255.255.252.0
- Cluster version:
6.5
In addition to this guide, you can use these documents:
Step 1 - Configuration
Step 1.1 - Interconnection of the three clusters
The first step is to interconnect the three clusters on the same OVHcloud vRack.
Use this guide to connect your clusters: Interconnect clusters through the vRack. To connect the three clusters, use the instructions provided in the guide:
- Datacenter 1 clusters in the vRack dedicated to Datacenter 3.
- Datacenter 3 clusters in the vRack dedicated to Datacenter 2.
When you have finished configuring your vRack, you will have these elements in your vRack:
- 9 dedicated servers (3 per cluster)
- 3 public IP addresses
- 3 Load Balancers
The three clusters are currently accessible from the Prism Central URL of each cluster.
Step 1.2 - Delete the Prism Central records for the Datacenter 1 and Datacenter 2 clusters
To implement a disaster recovery plan solution with Metro Availability, a cluster witness is required to automate tasks in the event of one of the clusters becoming unavailable. The cluster witness is located on a Prism Central virtual machine.
The Datacenter 3 cluster will host the Prism Central virtual machine for the three clusters, and serve as a cluster witness for the disaster recovery plan between Datacenter 1 and Datacenter 2.
Disabling Prism Central on the Datacenter 1 cluster
Connect via SSH to the Prism Element cluster in Datacenter 1 :
ssh nutanix@private_ip_address_prism_element_Roubaix
Enter Prism Element password
Run this command to remove Prism Element from the Prism Central configuration:
ncli multicluster remove-from-multicluster external-ip-address-or-svm-ips=private_ip_address_central_roubaix\
username=admin password=pwd_pe_Roubaix force=true
This message appears when disconnecting from Prism Central.
Cluster unregistration is currently in progress. This operation may take a while.
Enter this command:
ncli cluster info
NOTE: the value of the Cluster UUID that must have this form xxxxxxxx-xxxx-xxxx-xxxx-xxxxxxxxxxxx.
Disconnect from Prism Element and connect via SSH on the Prism Central virtual machine in Datacenter 1.
ssh nutanix@private_ip_address_prism_central_roubaix
Enter Prism Central password
Enter this command:
python /home/nutanix/bin/unregistration_cleanup.py cluster_uuid_prism_element_Roubaix
Disabling Prism Central on the Datacenter 2 cluster
Log in to the Prism Element cluster in Datacenter 2 via SSH.
ssh nutanix@private_ip_address_prism_element_Gravelines
Enter this command:
ncli multicluster remove-from-multicluster external-ip-address-or-svm-ips=private_ip_address_prism_central_Gravelines\
username=admin password=pwd_pe_Gravelines force=true
Enter this command:
ncli cluster info
Note the value of Cluster UID that should be in this form xxxxxxxx-xxxx-xxxx-xxxx-xxxxxxxxxxxx
Disconnect from Prism Element and connect via SSH on the Prism Central virtual machine in Datacenter 2.
ssh nutanix@private_ip_address_prism_central_Gravelines
enter Prism Central password
python /home/nutanix/bin/unregistration_cleanup.py cluster_uuid_prism_element_Gravelines
Step 1.3 - Registration of the two clusters on the Prism Central in Datacenter 3
Log in to the Prism Element in Datacenter 1 via SSH:
enter Prism Element password
Run this command:
ncli multicluster register-to-prism-central username=admin password=passwod_admin\ external-ip-address-or-svm-ips=private_ip_address_prism_central_Erith
This message appears:
Cluster registration is currently in progress. This operation may take a while.
Wait and enter this command:
ncli multicluster get-cluster-state
If the cluster is connected to Prism Central in Datacenter 3, you will see this information:
Registered Cluster Count: 1
Cluster Id : xxxxxxxx-xxxx-xxxx-xxxx-xxxxxxxxxxxx
Cluster Name : Prism-Central-Erith-FQDN
Is Multicluster : true
Controller VM IP Addre... : [private_ip_address_prism_central_Erith]
External or Masqueradi... :
Cluster FQDN :
Controller VM NAT IP A... :
Marked for Removal : false
Remote Connection Exists : true
Log in to Prism Element in Datacenter 2 via SSH:
ssh nutanix@adresse_ip_prism_element_Gravelines
Enter Prism Element password from Gravelines
Run this command:
ncli multicluster register-to-prism-central username=admin password=passwod_admin_Erith external-ip-address-or-svm-ips=private_ip_address_central_Erith
Cluster FQDN :
From a web browser, log in to the URL from Prism-Central to Datacenter 3, you will see the three clusters.
The Prism Central virtual machines in Datacenter 2 and Datacenter 1 are no longer being used. You can stop them.
In the main menu, click VMs
in the Compute & Storage submenu.
Select the Prism Central virtual machines in Datacenter 2 and Datacenter 1 and click Guest Shutdown
from the Actions
menu.
Step 1.4 - Verifying IP Addresses for iSCSI Connections on All Three Clusters
From the Prism Central dashboard, click the link to the Datacenter 3 cluster
On the Prism Element dashboard, click the cluster name
in the top left-hand corner.
Scroll down the window, verify the IP address under ISCSI Data Services IP, and click Save
From the Prism Central dashboard, click the link to the "Datacenter 2 cluster".
On the Prism Element dashboard, click "the cluster name" in the top left-hand corner.
From the Prism Central dashboard, click on the link to the "Datacenter 1 cluster".
On the Prism Element dashboard, click the "cluster name" in the top left-hand corner.
Step 1.5 - Creating Two Storage Containers
We will create two Storage Containers with the same name, one in Datacenter 1 and the other in Datacenter 2.
From the Prism Element main menu, click Storage Containers
submenu.
Click Create Storage Container
Type UsedForDR
in Name, choose the Datacenter 1 cluster
in Cluster, and click Create
Type UsedForDR
in Name, choose the Datacenter 2 cluster in Cluster
, and click Create
In the list of Storage Containers
, you will see two Storage Containers with the same name. One on the Datacenter 1 cluster and the other on the Datacenter 2 cluster.
Step 1.6 - Moving virtual machines to the Storage Container
We will move the virtual machine storage to the Storage Container
we have created.
Connect via SSH on the Prism Element of the Datacenter 1 cluster:
ssh nutanix@private_ip_address_Prism_element_Datacenter1
Enter the Nutanix account password of Prism Element
Run this command for each VM we will move to the Storage Container
, replacing vmname with the name of the virtual machine (in our disaster recovery plan, we have two virtual machines in Datacenter1, one on Windows and one on Linux).
acli vm.update_container vmname container=UsedForDR
Log in to the Prism Element of the Datacenter 2 cluster via SSH:
ssh nutanix@private_ip_address_Prism_element_Gravelines
Execute this command for each VM that we will move to the Storage Container
, replacing vmname with the name of the virtual machine (in our disaster recovery plan, we have three virtual machines in Datacenter 2, one on Windows, another on Linux, and the gateway that gives access to the Internet).
Step 1.7 - Creation of a category to be used when implementing the P.R.A.
We will create a category with two values in Prism Central to assign the virtual machines involved in replication.
Scroll through the main menu, click Categories
in the Administration
submenu.
Click New Category
Type Protected VM
in Name, add the <DATACENTER 1>
and <DATACENTER 2>
values in Values, and click on the next button Save
The category appears in the list and is ready to use.
Step 1.8 - Adding virtual machines in categories
We will assign two virtual machines on the Datacenter 1 cluster in one category and three virtual machines on the Datacenter 2 cluster in another category.
From the Prism Central main menu, click VMs
submenu.
Select the two virtual machines in Datacenter 1 on the left, then on the Actions
menu, and click Manage Categories
Add the category ProtectedVM: <DATACENTER 1>
, then click Save
Select the three virtual machines
in Datacenter 2 on the left, then Actions
Add the category ProtectedVM: <DATACENTER 2>
, then click Save
Step 1.9 - Setting up synchronous replications between Datacenter 1 and Datacenter 2
Synchronous replication allows permanent replication with 0 seconds of data loss.
Replication setup between Datacenter 1 and Datacenter 2
On the Prism Central main menu, click Protection Policies
in the Data Protection
submenu.
Click Create Protection Policy
Type <DATACENTER 1>-TO-<DATACENTER 2>
in Policy name, keep Local AZ
, and click Select Cluster
in Primary Location.
Choose the Datacenter 1 cluster and click Save
In the Disaster Recovery message, click Enable
The system checks that everything is correct before enabling Disaster Recovery.
Once the checks are complete, click Enable
to enable the Disaster Recovery option.
Click Enable
again.
Your Disaster Recovery option is being activated.
Keep Local AZ
, select the cluster in Recovery Location, and click Save
Click + Add Schedule
Choose Synchronous
for Protection Type and Automatic
for Failure Detection Mode. Then click Save Schedule
Click Next
Select the category ProtectedVM : <DATACENTER 1>
and click Add
Click Create
Virtual machines in Datacenter 1 are now replicated to Datacenter 2. You must wait for the first full replication to have permanent replication.
Replication setup between Datacenter 2 and Datacenter 1
Replication can be two-way. We will now create a replication from Datacenter 2 to Datacenter 1.
Choose as name <DATACENTER 2>-TO-<DATACENTER 1>
in Policy Name, keep Local AZ
, and choose Datacenter 2 cluster in Primary Location. Then click Save
Keep Local AZ, select the Datacenter 1 cluster, and click Save
Choose Synchronous
Click Next
Select the category ProtectedVM: <DATACENTER 2>
and click Add
Click Create
A second protection strategy is in place.
Step 1.10 - Create Subnets for Disaster Recovery Plan
We will create subnets that will be used to test disaster recovery plans.
For each existing subnet, a test network is required. On the two clusters of the Disaster Recovery Plan, we have three production subnets.
- based on VLAN 0.
- infrastructure on VLAN 1.
- production on VLAN 2.
We will therefore create three additional subnets on the Datacenter 2 and Datacenter 1 clusters with these names:
- testing on VLAN 100.
- testinfra on VLAN 101.
- production on VLAN 102.
Use this guide to create VLANs on your Nutanix clusters: isolate production management machines.
In the Prism Central Subnets
dashboard, you will see six new subnets.
Step 1.11 - Implementation of disaster recovery plans
Now that the replications and subnets are in place, we will implement automated or manual disaster recovery plans on demand to:
- migrate virtual machines on the fly between the two clusters
- Test that replication is working properly
- Automatically restart the VMs that are members of the P.R.A. in the event of a failure of one of two clusters.
Creation of a disaster recovery plan for the Datacenter 1 cluster
In the main menu of Prism Central, click Recovery Plans
submenu.
Click on Enable Disaster Recovery
on the left.
Normally, the recovery plan must be activated as indicated with the message Disaster Recovery enabled. Click on the right to close this window.
Click Create New Recovery Plan
Choose this information:
Recovery Plan Name:
Recovery VM from <DATACENTER 1> to <DATACENTER 2>
Primary Location:
Local AZ
Primary Cluster:
Recovery Location:
Local AZ
Recovery Cluster:
Failure Execution Mode:
Automatic
Execute failover after disconnectivity of:
30 seconds
Then click Next
Click + Add VM(s)
Select both virtual machines and click Add
Click Next
Click OK. Got it
Click Stretch networks
Click Proceed
Choose the VLANs that will be used during the IP like this:
Primary
Production
production
Test Failback:
testproduction
Production
Recovery
Production:
production
Test Failback:
testproduction
Production:
Then click Done
The Disaster Recovery Plan has been created for the Datacenter 1 site. Click Create Recovery Plan
to create the Datacenter 2 Disaster Recovery Plan.
Recovery Plan Name:
Recovery VM from <DATACENTER 2> to <DATACENTER 1>
Primary Location:
Local AZ
Primary Cluster:
Recovery Location:
Local AZ
Recovery Cluster:
Automatic
30 seconds
Then click Next
Click + Add VM(s)
Select the three virtual machines and click Add
Click Next
Click Proceed
Primary
Production:
basis
Failback test:
test
Production:
Recovery
Production:
basis
Failback test:
test
Production:
Then click + Add Network Mapping
Primary
Production
infra
Test Failback:
testinfra
Production
Recovery
Production:
infra
Test Failback:
testinfra
Production:
Primary
Production:
production
Test Failback:
testproduction
Production:
Recovery
Production:
production
Test Failback:
testproduction
Production:
Then click Done
Both disaster recovery plans are in production.
Step 2 - Validate Disaster Recovery Plan
Step 2.1 - Monitoring the Disaster Recovery Plan
Using the Commit to Disaster Recovery Plan Option
You can validate the disaster recovery plan via Prism Central.
Click on the Recovery VM from Datacenter 1
to validate and test.
Click Validate
Select the Datacenter 1 cluster for Entity Failing Over From and the Datacenter 2 cluster for Entity Failing Over To. Then click Proceed
The recovery plan has been validated. Click Close
Test Disaster Recovery Plan
We can test the disaster recovery plan without impacting production. The test creates virtual machines with different names on the destination cluster in the VLANs created earlier.
Click Test
Select the Datacenter 1 cluster for Entity Failing Over From and the Datacenter 2 cluster for Entity Failing Over To. Then click Test
Click Execute Anyway
Go to the VM dashboard in Prism Central and you will see the test virtual machines that are created with the replicated data.
Return to your recovery plan and click Clean-up test entities
to remove the test virtual machines.
Click Clean Up
Step 2.2 - Live migration of Datacenter 1 virtual machines in Datacenter 2
On a fully operational infrastructure, it is possible to move virtual machines from one cluster to another without any service downtime.
Go to a virtual machine in Datacenter 1 that is part of the recovery plan. We will ping the OVHcloud DNS server 213.186.33.99.
Return to your recovery plan and open the More
menu, then click Failover
Choose Planned Failover
, then select the Live Migrate Entities
box.
Then click Failover
Type Failover
and click Failover
Hot migration is in progress.
The migration was completed successfully without any service downtime.
You can go back to the virtual machine and see that the ping continues to work even if the virtual machine has been moved from one cluster to another.
Step 2.3 - Operations after a hot migration
After a migration, it is necessary to reverse the replication and operation of the disaster recovery plan.
Reverse Replication
On the Prism Central main menu, click Protections Policies
submenu.
Click on the protection plan named <DATACENTER 1> TO <DATACENTER 2>
Click Update
Position the mouse below the Datacenter 1 cluster name in Primary Location and click Edit
Check the <DATACENTER 2>
cluster instead of the Datacenter 1 cluster.
Click Save
Click Update Location
Position the mouse below the Datacenter 2 cluster name in Recovery Location and click Edit
Select the <DATACENTER 1>
cluster instead of the Datacenter 2 cluster.
Click Save
Click Next
Click Update
Replication is reversed, click the button to close the protection plan.
Disaster Recovery Plan Reverse
submenu.
Click Recovery VM from <DATACENTER 1> to <DATACENTER 2>
On the More
menu, click Update
In locations, put the Datacenter 2 cluster in Primary Clusters and the Datacenter 1 cluster in Recovery Clusters and then click Next
Click Proceed
Click Next
Primary
Production:
production
Test Failback:
testproduction
Production:
Recovery
Production:
production
Test Failback:
testproduction
Production:
Click Done
To return to the original state, you need to perform a hot migration again and reverse replication and the disaster recovery plan. You can use this part of the guide if your disaster recovery plan is triggered because a cluster is unavailable.
Step 2.4 - Execute the Disaster Recovery Plan in Real Condition
We will simulate a total loss of connection to Datacenter 2 where three virtual machines are located in the disaster recovery plan (the Internet gateway and two other virtual machines).
Log in to the command line and ping the public address of the gateway.
## Ping from a remote linux console
ping xx.xx.xx.xx
Reply from xx.xx.xx.xx: bytes=32 time=21ms TTL=58
Reply from xx.xx.xx.xx: bytes=32 time=23ms TTL=58
Reply from xx.xx.xx.xx: bytes=32 time=20ms TTL=58
Leave the ping command to run continuously and return to Prism Central.
submenu.
The three virtual machines in the disaster recovery plan are functional.
All three nodes in the Datacenter 2 cluster will be disconnected.
Return to the console that is pinging to the gateway, and you will see a connection loss.
Request timed out.
Request timed out.
Request timed out.
Request timed out.
In Prism Central, click the top right on the tasks
to display the task launch, including Recovery plan execute.
However, it will take a while for the virtual machines to reboot on the other cluster. In this guide, three virtual machines are restarted on the remote cluster. It will take you 4 minutes to start the virtual machines. This time can be measured by regularly running tests on disaster recovery plans.
Go back to the text console and you will see that the ping works again.
Request timed out.
Reply from xx.xx.xx.xx: bytes=32 time=19ms TTL=58
Reply from xx.xx.xx.xx: bytes=32 time=18ms TTL=58
Go to Prism Central in the virtual machine management, you will see the three virtual machines of the recovery plan in duplicate. They are marked as started, but in reality, only the ones restarted in Datacenter 1 are working.
We will reconnect the three nodes in the vRack to return to normal mode.
After the recovery, the virtual machines on the original cluster are still visible but are turned off. You can delete or keep them if problems occur on the VMs that are being rebooted.
You can view the history of Disaster Recovery actions in Prism Central.
Click the button in the top right-hand corner to go to the Prism Central configuration.
Left-click Witness
and click View Usage History
The list of events appears, click Close
to close.
For more information and tutorials, please see our other Nutanix support guides or explore the guides for other OVHcloud products and services.